When I get the spec sheets on mechanical units I need to circuit, the specs usually show Minimum Circuit Amps (MCA) and Maximum Overcurrent Protection (MOP). I always do a calc using the raw data to make sure the MCA and MOP look correct. The following are the specs on a packaged unit I received today.
Compressor 1 RLA - 23 amps
Compressor 2 RLA - 27.5 amps
Supply Fan FLA - 18.9 amps
Condenser Fans FLA - 10.5 Amps (3 x 3.5)
Heater FLA - 86.6 amps
Specs give MCA of 111.47 and MOP of 125 amps.
This heat and cooling will not run concurrently with this unit. So, largest running load will be heater and supply fan.
My MCA would be: 86.6 A x 1.25 + 18.9 amps= 127.15 amps. Breaker would be 130 amps.
The only way their numbers work would be to treat the heat load as a non-continuous load. I could not find any support for considering the heat in this case as a non-continuous load. Searched around on this site an other resources and found nothing to support it as a non-continuous load.
Am I missing something?
Compressor 1 RLA - 23 amps
Compressor 2 RLA - 27.5 amps
Supply Fan FLA - 18.9 amps
Condenser Fans FLA - 10.5 Amps (3 x 3.5)
Heater FLA - 86.6 amps
Specs give MCA of 111.47 and MOP of 125 amps.
This heat and cooling will not run concurrently with this unit. So, largest running load will be heater and supply fan.
My MCA would be: 86.6 A x 1.25 + 18.9 amps= 127.15 amps. Breaker would be 130 amps.
The only way their numbers work would be to treat the heat load as a non-continuous load. I could not find any support for considering the heat in this case as a non-continuous load. Searched around on this site an other resources and found nothing to support it as a non-continuous load.
Am I missing something?