I'm good with branch feeder and branch motor circuit calculations with respect to NEC. However, I've always had a nagging question about circuit protection methodology that I've seen engineers employ when it comes to control (non-motor) circuits. I don't get the opportunity to actually design and specify control panels, so I'm a bit puzzled by some of the things I've seen.
For example, when it comes to VFDs and servo drives, for example, I recognize that you forget about the motor, itself, and focus on the current that the drive is drawing.
As a simple example, imagine you have 5 servo drives that list an FLA of 9.4A, each. Now, in your application, none of your servos operate at full load, and your current draw at the input of the drive never even comes close to the listed FLA.
According to 210.20(A) and 215.3, the overcurrent device must be sized no less than 100% of the non-continuous load plus 125% of the continuous load. In this example, there are no continuous loads. The servos make infrequent, short duration moves, and the current draw of the drive never exceeds 0.5A. With such a paltry amount of current draw, can they even be considered a non-continuous load, by strict definition?
It seems to me that in order to be compliant with NEC, each drive circuit should be protected with a 10A fuse. I never see other engineers protecting circuits like these with such a "large" fuse. In fact, I'm looking at a set of prints, now, where seven servo drives are ALL being fed from a 15A fuse. What's the most correct approach? Protect each with a fuse that is based on their FLA?
One more question -- suppose I wish to protect the feeder circuit that supplies power to these five servo drives. Should I be looking at a 50A fuse?? While that seems to be what the code requires, I've never understood the way that other engineers size upstream circuit protection.
I mean, how is it reasonable to have 10 non-motor branch circuits, each protected with a 15A fuse, and have all those branch circuits fed from a 60A breaker?
Am I missing something?
Thanks for reading.
For example, when it comes to VFDs and servo drives, for example, I recognize that you forget about the motor, itself, and focus on the current that the drive is drawing.
As a simple example, imagine you have 5 servo drives that list an FLA of 9.4A, each. Now, in your application, none of your servos operate at full load, and your current draw at the input of the drive never even comes close to the listed FLA.
According to 210.20(A) and 215.3, the overcurrent device must be sized no less than 100% of the non-continuous load plus 125% of the continuous load. In this example, there are no continuous loads. The servos make infrequent, short duration moves, and the current draw of the drive never exceeds 0.5A. With such a paltry amount of current draw, can they even be considered a non-continuous load, by strict definition?
It seems to me that in order to be compliant with NEC, each drive circuit should be protected with a 10A fuse. I never see other engineers protecting circuits like these with such a "large" fuse. In fact, I'm looking at a set of prints, now, where seven servo drives are ALL being fed from a 15A fuse. What's the most correct approach? Protect each with a fuse that is based on their FLA?
One more question -- suppose I wish to protect the feeder circuit that supplies power to these five servo drives. Should I be looking at a 50A fuse?? While that seems to be what the code requires, I've never understood the way that other engineers size upstream circuit protection.
I mean, how is it reasonable to have 10 non-motor branch circuits, each protected with a 15A fuse, and have all those branch circuits fed from a 60A breaker?
Am I missing something?