Mgarf33
Member
- Location
- Virginia Beach, Va
I have a customer with an existing 50A hot tub circuit, using NM-B 6awg 3 wire w/g.
The customer wishes to remove this hot tub permanently. They are adding 2 new components; a 120v 15A dehumidifier, and a 240v 15A mini-split heat pump that are in the location of the existing disconnect. I would like to use an outdoor sub panel to split the 2 circuits.
My issue is, I can't readily find a NEMA 3R box at Home Depot, are the Eaton BR panels rated for outdoor use ok for this project?
Also, I would need an additional grounding bar correct, as they only come with one neutral bar with an optional bonding screw.
I would only bond the new ground terminal bar and not the neutral bar.
Any issues with this?