That being said, if you run #6 for voltage drop or any reason unrelated to ampacity, you have to proportionally upsize the EGC. In this case, it means it would be the same size as the rest of the conductors.
Y would you say a #6 is needed if you upsize for voltage drop do you not use 250.122 table to size the egcThe #6 is above and beyond what the NEC requires for ampacity reasons, unless there is a serious factor like high ambient temperature, or extreme conductor bundling, or both.
#12 is what the NEC requires for a 20A circuit. The 15A fused disconnect downstream doesn't override this, until you get downstream of it.
That being said, if you run #6 for voltage drop or any reason unrelated to ampacity, you have to proportionally upsize the EGC. In this case, it means it would be the same size as the rest of the conductors.
Table 250.122 is the general rule. 250.122(B) would apply if upsizing for voltage drop, and it would require 6 AWG EGC in OP's situation if conductors are sized like they are because of voltage drop.Y would you say a #6 is needed if you upsize for voltage drop do you not use 250.122 table to size the egc