And what happens when you happen to get a breaker that wont trip? you can possibly damage the wiring of the circuit by loading it to the point the breaker should trip which is higher then the handle rating of a given breaker, take a look at breaker trip curves then add the impedance of a bad connection or even a long circuit run and you can have a problem.
I knew a guy who had a simple switch and cord set up to find breakers, until he ran into a breaker that wouldn't trip and set the house on fire, you never know how good the connections are between the point you run your test and the panel, or if there are any open splices in the walls along the way.
Doing test like this on customers houses is a quick way to subject yourselves and company to high liability should something go wrong.
To do this to test breakers at the panel is one thing but at the load end of a circuit is just not a good idea.
There are many methods of safe testing to detect bad connections that don't involve using high current loading, low resistance testing (below 1 ohm) has been done for years, but it can be hard if the exact length of the circuit is not known, but voltage drop testing will have the same problem with the added problem of causing high temperatures at a unknown bad connection that could cause a fire.
To test for a utility side connection is done like this as I have done it also, but with the circuit breakers in the panel shut off in case there is a bad neutral connection which could over voltage customers appliances, many times I have to lift the water pipe ground as it would mask the neutral problem on houses with common water lines to other houses also connected to the same transformer, the problem is it is possible to cause over voltages at a neighbors house if the bad neutral connection is ahead of the point the drops splits up at the pole and they don't have a good water pipe ground, if I see this then I let the utility put in a loader so I wont be liable, but it can be tricky, because if your not there to lift the water ground and turn off the circuit breakers when they do the test they will assume there is no problem as the water pipe will mask the neutral problem.