Circuit Tracers for Dead Circuits

Merry Christmas
Status
Not open for further replies.

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
What's the best you guys have seen for dead circuit tracers? I've chased my tail a few times lately, looking for circuits on dead receptacles. Some were never labeled at all, some had faded labels, some had been moved to other circuits.
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
Say if the hot side was open on a 120V receptacle, you could connect the tracer's transmitter terminals between the neutral conductor and the metal box or conduit. That should create a current through the neutral conductor back to the N/G bond so that you may be able identify the neutral with the receiver inside of a panel or another box. Once you find a particular neutral conductor you could pull it away from the panel or box to get a better confirmation by the receiver that it's the one. Then you could see which conduit that this neutral conductor goes to, which at least narrows it down to a fewer number of hot conductors/circuits where the break should be. Then you'd use your other techniques to go from there with the process of elimination, etc.
Maybe you're already doing something like this, in which case never mind. :)
 

rambojoe

Senior Member
Location
phoenix az
Occupation
Wireman
A wirenut works awesomely.
Ok, i guess i should explain... A wirenut and a continuity tester works super great.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
If it is a circuit that is feed off a gfi receptacle, then unfortunately the neutral will be open if it’s tripped, so the battery trick will not work. But at least with the battery hack, you can narrow down to which panel it’s from if the neutral is not compromised.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
An extension cord plugged into a known-properly-wired receptacle along with a solenoid tester make a great troubleshooting combination.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I use this all the time to trace. It gives me an approximate length of the circuit and I use it with the tone tracer probe to trace the circuit. If the circuit is accidentally energized (I think is 120V max) the unit will not get damaged.


Screen Shot 2023-02-15 at 7.14.34 PM.png
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
I use an ideal sure trace. It's not perfect but it works better than any thing I've used in the past. Much much better than my fluke tonner
 