This concerns a call I received from a client and is on the "practical" side of what I do (EE).
The client has an office in his 200-year-old farmhouse. It was originally wired with BX probably in the '30's, which in the course of renovations 25 years ago, was 90% replaced with NM with ground along with some new work, all on Square D QO panels.
The garage area (originally carriage area and hay storage) had new work with after the original BX. This was done in ungrounded NM and in some locales, with steel boxes that were never grounded. When the renovations were done 25 years ago, most of the boxes (except one) had at least one grounded NM run to each box, grounding all boxes except one. This happened a new door was put, requiring the existing circuits be interrupted (with extensions around the new door) with two new junction boxes. Given that 3 circuits run through these in a 4" square boxes with a plaster rings to allow a single blank plate, access is "problematic". The client says the entire area was opened up (having been done in old varnished knotty pine) and then replaced.
The specific problem is this... the lights to garage office are on 3-way, 4-way, 3-way switch circuit with the last switch (at the end) with two traveler (red, white) wires, and a return (black) to 4-way's junction box to feed the lights. That switch has not been used in years (and happened to be the run done in "original" ungrounded NM). However, it was accidentally flipped one day, rendering the other 3-way and the 4-way useless. Thus led to a search as what caused the "outage" - a flipped switch in out-of-the-way garage corner (problem temporarily solved) but still in need of a "definitive" fix.
Measuring the voltage on the first 3-way and the 4-way was as expected (analog). However, the measurements at the remote 3-way showed the white traveler wire as expected (0 or 120 v when the other switches were flipped), but the red traveler wire was about 10 v (the ground reference was through the garage door frame, admittedly, not the best ground in the world, but the best available at the time). My thought about this was some inductive voltage from white traveler wire, or some kind of ground loop.
For simple tracing on non energized tracing, I have a Klein Tools Tone & Probe Test and Trace Kit (VDV500-705) and a Harbor Freight Cen-Tech Cable Tracker (94181).
I tried tracing the red traveler backwards, hoping to find where the interruption is, without going to the two 4" junction boxes, or either the near 3-way or the 4-way and unscrewing wirenuts and doing a simple de-energized continuity with a 40' piece of wire. Unfortunately, neither of these testers was terribly helpful, either using a single wire signal feed (red traveler), or a second feed (the white traveler or the black return).
Any thoughts on this. I'm not anxious to let my client know that the electrician who did this 25 years ago may have mis-wired this, but "it is what is".
Another question is - can one "date" when the garage area was wired with unground NM (roughly speaking)?
My thanks in advance.
The client has an office in his 200-year-old farmhouse. It was originally wired with BX probably in the '30's, which in the course of renovations 25 years ago, was 90% replaced with NM with ground along with some new work, all on Square D QO panels.
The garage area (originally carriage area and hay storage) had new work with after the original BX. This was done in ungrounded NM and in some locales, with steel boxes that were never grounded. When the renovations were done 25 years ago, most of the boxes (except one) had at least one grounded NM run to each box, grounding all boxes except one. This happened a new door was put, requiring the existing circuits be interrupted (with extensions around the new door) with two new junction boxes. Given that 3 circuits run through these in a 4" square boxes with a plaster rings to allow a single blank plate, access is "problematic". The client says the entire area was opened up (having been done in old varnished knotty pine) and then replaced.
The specific problem is this... the lights to garage office are on 3-way, 4-way, 3-way switch circuit with the last switch (at the end) with two traveler (red, white) wires, and a return (black) to 4-way's junction box to feed the lights. That switch has not been used in years (and happened to be the run done in "original" ungrounded NM). However, it was accidentally flipped one day, rendering the other 3-way and the 4-way useless. Thus led to a search as what caused the "outage" - a flipped switch in out-of-the-way garage corner (problem temporarily solved) but still in need of a "definitive" fix.
Measuring the voltage on the first 3-way and the 4-way was as expected (analog). However, the measurements at the remote 3-way showed the white traveler wire as expected (0 or 120 v when the other switches were flipped), but the red traveler wire was about 10 v (the ground reference was through the garage door frame, admittedly, not the best ground in the world, but the best available at the time). My thought about this was some inductive voltage from white traveler wire, or some kind of ground loop.
For simple tracing on non energized tracing, I have a Klein Tools Tone & Probe Test and Trace Kit (VDV500-705) and a Harbor Freight Cen-Tech Cable Tracker (94181).
I tried tracing the red traveler backwards, hoping to find where the interruption is, without going to the two 4" junction boxes, or either the near 3-way or the 4-way and unscrewing wirenuts and doing a simple de-energized continuity with a 40' piece of wire. Unfortunately, neither of these testers was terribly helpful, either using a single wire signal feed (red traveler), or a second feed (the white traveler or the black return).
Any thoughts on this. I'm not anxious to let my client know that the electrician who did this 25 years ago may have mis-wired this, but "it is what is".
Another question is - can one "date" when the garage area was wired with unground NM (roughly speaking)?
My thanks in advance.