aftershock
Senior Member
- Location
- Memphis, TN
Nice trouble call I got going here.
Customer has a circuit which controls the upstairs receptacles.
MWBC
10 rec on this circuit (give or take 1)
Other circuit is for a heater/fan/light combo in bath.
2 TVs, 2 VCRs, 2 lamps, 2 printers, 1 computer, 2 or 3 table clocks.
3 UPS (Uninterrupted Power Supply)
1 is a apc Model BE500R. Namplate shows input: 115 volts 12 amps
2 are apc model BE350G input 115 volts 8 amps
I have already found and remade wire joints in the homerun box and we checked every receptical outlet. It has never tripped while I was there and the circuit was only drawing 5 amps at the most with everything running.
The 2 UPS listed I find hard to believe draw that much amperage and if the do then they are doing it at a time when I am not there. But this is the only thing I can think of that would be the problem. I figured I would run it by you fine folks on this forum.
Customer has a circuit which controls the upstairs receptacles.
MWBC
10 rec on this circuit (give or take 1)
Other circuit is for a heater/fan/light combo in bath.
2 TVs, 2 VCRs, 2 lamps, 2 printers, 1 computer, 2 or 3 table clocks.
3 UPS (Uninterrupted Power Supply)
1 is a apc Model BE500R. Namplate shows input: 115 volts 12 amps
2 are apc model BE350G input 115 volts 8 amps
I have already found and remade wire joints in the homerun box and we checked every receptical outlet. It has never tripped while I was there and the circuit was only drawing 5 amps at the most with everything running.
The 2 UPS listed I find hard to believe draw that much amperage and if the do then they are doing it at a time when I am not there. But this is the only thing I can think of that would be the problem. I figured I would run it by you fine folks on this forum.