Can someone please elborate on this for me?
I have two notes on my drawings
1. All branch circuits shall have a dedicated full sized neutral conductor.
Does this mean what it says that I need a separate neutral for every circuit. I was uinder the impression that you can sometimes share a neutral for up to threee circuits.
2. Furnish and install a green insualted copper ground conductor in all power feeder conduits with a phase & neutral conductors.
So this means exactly what it says but for FEEDERS only.
Thanks for the help