The 2002 NEC Article 422.10(A) last sentence states that"the branch circuitsof householdcooking appliances shallbe permitted to be in accordance with Table 220.19. Recently I have had a number of clients compaining about range circuit breakers frequently tripping. In most cases the ranges were in 12 kW to 13.5 kW sizes and were powered from 40 circuits. This appears to be OK with article 422.10 and Table 220.19.
Actual measured curent for each of the client's typical cooking situations was frequently in the 50 ampere range. No wonder the breakers were tripping. So much for derating.
Upgrading the circuits to 50 amperes would likely resolve the problems, but I can't understand why the NEC would permit 40 ampere circuits to be installed when normal range usage could result in current draws in excess of 50 amperes.
Can anyone shed some light on the "problem"??
Actual measured curent for each of the client's typical cooking situations was frequently in the 50 ampere range. No wonder the breakers were tripping. So much for derating.
Upgrading the circuits to 50 amperes would likely resolve the problems, but I can't understand why the NEC would permit 40 ampere circuits to be installed when normal range usage could result in current draws in excess of 50 amperes.
Can anyone shed some light on the "problem"??