Circuits form emergency generator & UPS in same race

Status
Not open for further replies.

hassaf

Member
If the emergency generator feeds a panel, and lets say that same panel feeds a UPS system, can both circuits, from UPS and from Panel be installed in the same raceway?
 
Re: Circuits form emergency generator & UPS in same race

Lets make sure we are taking about an Art 700 application, not an Art 701 or 702 one. Review the scope of each article and then let us know. Not all generators are emergency generators. What its for determines the type, the type determines the wiring in the building.
 
Re: Circuits form emergency generator & UPS in same race

Thanks for asking the question.

This falls under section 702, and after reviewing the section, it would seem that both system can be installed in the same raceway.
 
Re: Circuits form emergency generator & UPS in same race

702 is optional, therefore you are correct you can mix and match what ever you want.
 