Do the requirements of 517 extend to the area above the ceiling for circuits feeding the required receptacle of a rooftop unit? After reading 517 I would say no. I'm just going by the definition of Patient Care Area(and related info in 517) and haven't been able to find where this is addressed in 517.
Thanks
 
Re: Circuits passing thru Patient care Area

I believe any circuit that is not intended to serve the patient care area is not required to meet the requirements of 517 part II per 517.10(B)(1). :)
 