Re: Cistern Float
Thanks everyone for your replies. It looks to me like this float type of control that I have described is ok to use if all of the other wiring meets the code. This goes along with the way a well supply place and several well people around here said they do it in WI and MN.
In this application, the submersible pump is a 1/2 HP at around 5-6 amps and I believe that it is fed from a 20 amp double pole breaker. The float cord wire size is #16. According to table 430-72(b) column C, it looks like the float cord should be a #14 wire. What about the ground fault protection that they mention there? Is that considered the circuit breaker? The reason that I became involved and decided to ask about this, is because the float switch cord was exposed and damaged. It was not protected according to code. Actually the whole thing needs to be rewired as the power to the outside controller is supplied with a hanging cord.