klineelectric
- FL
- electrical contractor
This is not my interpretation, they make us put arc fault on EVERY outlet that doesn't require GFCI. I guess even though " garage, laundry, bathroom, etc are defined in art.100 of the NEC , the codemakers FORGOT to list these areas with all the others in 210.12
07/21/2010
CITRUS COUNTY BUILDING DIVISION
NOTICE
JULY 13, 2010
To: Electrical contractors, general, building and residential contractors,
owner/builders, and interested parties
Subj: 2008 NEC 210.12 ? ARC Fault Protection
The following constitutes our interpretation and application of 2008 NEC 210.12 ?
ARC Fault Protection:
? All single phase 120 volt 15 and 20 ampere branch circuits supplying outlets,
(NEC 100 defines outlets to include receptacles, lighting and smoke
alarms installed in dwelling units)
? Family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms,
sunrooms, recreation rooms, closets, hallways, or similar rooms or areas
shall be protected by a UL approved combination type ARC fault breaker
? Branch circuits that supply power to receptacles that are required to be
GFCI protected per NEC 210.8-1 thru 8 are exempt from ARC fault
protection. These areas include kitchen countertops, bathrooms, unfinished
basements, laundry rooms, garages and outdoors.
Lighting outlets in the aforementioned area shall be ARC fault protected
Fixed in place appliance circuits such as washing machine, microwave oven,
garbage disposal, and dishwasher are exempt from ARC fault protection as well
as GFCI protection. If sink is within 6? of washing machine then GFCI required
on washer receptacle.
Kitchen refrigerator receptacles will be ARC fault protected
240 Volt circuits are exempt from ARC fault protection
07/21/2010
NOTICE
JULY 13, 2010