Re: CL2 wire in junction box with CL1 wire
...Class 1 (Romex) seems to be overkill for 12 VDC and may make it comercially unattractive.
Maybe so BUT you can come out of your enclosure to a wiring compartment or J box with 18ga TFFN then splice it to anything you want. As long as the wiring in the enclosure with the line voltage wiring is of the same voltage rating.
Another possibility is to have a separate LV wiring compartment within the enclosure or an external terminal block on the back or side of the enclosure.
Stuff like this is designed all the time, shouldn't be a big deal.
[EDIT]
Ahh, Ok, I just reread your original post and see that you said: ...The device has separate connections for each and sits in a standard junction box.
This does present the problem that the J box is then your encloure (and I assume that this is meant also to be installed on existing wall boxes) and what I said above really is not applicable unless you design your product to fit on or over the J box with part of it overhanging say to one side (the larger dimmers do this). The overhang would allow for the LV connection outside of the box and would allow the use of any type of wire and make wiring easier since it doesn't have to be fished into the box.
Not quite as elegant as something smaller but I can't think of any way you would be allowed to bring LV wiring into the box otherwise unless it were, like you say Romex or similar.
[ February 17, 2004, 08:42 PM: Message edited by: hbiss ]