250.68(C)(2) reads:
(2) The metal structural frame of a building shall be permitted to be used as a conductor to interconnect electrodes that are part of the grounding electrode system, or as a grounding electrode conductor.
Hold-down bolts securing the structural steel column that are connected to a concrete-encased electrode that complies with 250.52(A)(3) and is located in the support footing or foundation shall be permitted to connect the metal structural frame of a building or structure to the concrete encased grounding electrode. The hold-down bolts shall be connected to the concrete-encased electrode by welding, exothermic welding, the usual steel tie wires, or other approved means
For clarification: Can we look at this as two different statements. In other words, can I use the structural frame of the building as a grounding electrode conductor to interconnect electrodes (period)
OR
can I only use it to interconnect electrodes IF the provisions of the 2nd part are met (hold down bolts connected to UFER) ??
(2) The metal structural frame of a building shall be permitted to be used as a conductor to interconnect electrodes that are part of the grounding electrode system, or as a grounding electrode conductor.
Hold-down bolts securing the structural steel column that are connected to a concrete-encased electrode that complies with 250.52(A)(3) and is located in the support footing or foundation shall be permitted to connect the metal structural frame of a building or structure to the concrete encased grounding electrode. The hold-down bolts shall be connected to the concrete-encased electrode by welding, exothermic welding, the usual steel tie wires, or other approved means
For clarification: Can we look at this as two different statements. In other words, can I use the structural frame of the building as a grounding electrode conductor to interconnect electrodes (period)
OR
can I only use it to interconnect electrodes IF the provisions of the 2nd part are met (hold down bolts connected to UFER) ??