Pardon my ignorance as I'm working practice problems for the upcoming PE exam and came across an area of confusion. Thus, I'm here for your infinite wisdom.
For a 120/240V, three wire, single phase copper feeder of Type THW, I'm required to size a feeder wire given a net computed load of 68.3 amps for a single family dwelling unit. However according to NEC article 230.79(C), a 100A rating for the disconnect means is required for a one-family dwelling unit and therefore the minimum load is 100A. Now here is where things go wonky. The solution refers to Table 310.15(B)(6), which I could not find in NEC 2014. A quick search online indicates that there WAS a Table 310.15(b)(6) in a previous edition and that for a 100A feeder rating, you would select 4AWG copper as seen on this site <http://freenec.com/T124.html> and thus the answer to the problem. Case closed.
But again there is no table 310.15(b)(6) in NEC 2014. Thus I refer to section 310.15(B)(7)(2) in NEC 2014, which states that the feeder conductors shall have an ampacity not less than 83% of the feeder rating. This then becomes 83% of 100A, which is 83A. I then refer to Table 310.15(b)(16), look at 75C for THW, and identify that for a 4AWG conductor, its allowable ampacity is 85A, which would work as the answer. I used the following link as a basis for this conclusion <http://iaeimagazine.org/magazine/2014/05/04/2014-national-electrical-code-updates-wire-and-cable/>
My questions to you because ignorance is not bliss and that this will deprive me of sleep:
1. Confirm or deny - there is no table 310.15(b)(6) in NEC 2014 and that I'm not blind.
2. Was my conclusion and conductor selection accurate based on the NEC 2014 code?
Thanks for your input!
For a 120/240V, three wire, single phase copper feeder of Type THW, I'm required to size a feeder wire given a net computed load of 68.3 amps for a single family dwelling unit. However according to NEC article 230.79(C), a 100A rating for the disconnect means is required for a one-family dwelling unit and therefore the minimum load is 100A. Now here is where things go wonky. The solution refers to Table 310.15(B)(6), which I could not find in NEC 2014. A quick search online indicates that there WAS a Table 310.15(b)(6) in a previous edition and that for a 100A feeder rating, you would select 4AWG copper as seen on this site <http://freenec.com/T124.html> and thus the answer to the problem. Case closed.
But again there is no table 310.15(b)(6) in NEC 2014. Thus I refer to section 310.15(B)(7)(2) in NEC 2014, which states that the feeder conductors shall have an ampacity not less than 83% of the feeder rating. This then becomes 83% of 100A, which is 83A. I then refer to Table 310.15(b)(16), look at 75C for THW, and identify that for a 4AWG conductor, its allowable ampacity is 85A, which would work as the answer. I used the following link as a basis for this conclusion <http://iaeimagazine.org/magazine/2014/05/04/2014-national-electrical-code-updates-wire-and-cable/>
My questions to you because ignorance is not bliss and that this will deprive me of sleep:
1. Confirm or deny - there is no table 310.15(b)(6) in NEC 2014 and that I'm not blind.
2. Was my conclusion and conductor selection accurate based on the NEC 2014 code?
Thanks for your input!