Ran into an issue on a job. We have a 400 amp fused disconnect outside, next to the meter, and want to run two 3/0 feeder taps into two separate 200 amp main breaker panels in two separate raceways. The panels are inside the building, so the tap conductors will be originating outside and after entering the building will travel about 12-15 feet where they terminate in the main breaker panels. The overall length of these feeder taps would be well under 25'.
I have been told that these feeder taps must terminate at the nearest point of entrance according to 240.21(B)(5). This would mean that the panels would need to be relocated to where the feeder taps/raceway enter the building. Normally, would not be a problem, but the two panels are already made up and have all circuits landed, etc.
The 25' tap rule does not stipulate taps made inside, outside or entering inside from the outside.
Would the 25' tap rule apply to this installation, or am I required to locate those panels at the nearest point to where the feeder taps enter the building?
(We are considering removing the 400 amp disconnect and replacing it with two 200 amp disconnects to protect the 3/0 wires as normally done with feeders)
I have been told that these feeder taps must terminate at the nearest point of entrance according to 240.21(B)(5). This would mean that the panels would need to be relocated to where the feeder taps/raceway enter the building. Normally, would not be a problem, but the two panels are already made up and have all circuits landed, etc.
The 25' tap rule does not stipulate taps made inside, outside or entering inside from the outside.
Would the 25' tap rule apply to this installation, or am I required to locate those panels at the nearest point to where the feeder taps enter the building?
(We are considering removing the 400 amp disconnect and replacing it with two 200 amp disconnects to protect the 3/0 wires as normally done with feeders)