Clasified or Not Clasified ?

Status
Not open for further replies.

donnie

Member
Location
Kentucky
A quick-lube and a brake repair and tire ballancing garage, would the area described in art.511.3 (B) (1) apply , If so do you think the overhead garage doors going up and down would meet the exception for rate of air changes.There are usually 4 to 5 , 9'x16' doors.


Just wondering about opinions.
Thanks:
 

earlydean

Senior Member
Re: Clasified or Not Clasified ?

yes, it is classified up to 18 inches, and no the OH door is not considered mechanical ventillation.
 