• We will be performing upgrades on the forums and server this weekend. The forums may be unavailable at times. Thank you for your patience and understanding as we work to make the forums even better.
Class 1 Circuits....
I've been digging for information on when a circuit must be marked as a Class 1 circuit...
For instance, PLC circuits, which are fed off the cards and generally powered from the backplane/power supply which is not marked as a Class 2 or 3 power source and generally falls under the 30V/1000VA ratings... and could definately be considered as remote control and signalling...
So, would these be required to be marked as Class 1 or is it an optional marking?
Yes, Class 2 and Class 3 equipment is almost always marked, with a few exceptions... Class 1 equipment on the other hand is typically not ever marked. In fact, there are no equipment marking requirements, only Class 1 circuits are required to be indentified per NEC 725.10. Also, per UL508a, a Class 1 circuit has to have certain markings applied to it as well. While in my opinion, these circuits could be considered Class 1 circuits, I have never seen a UL508a listed PLC panel come into the field marked that way. In fact, I've never seen a Class 1 circuit marking used anywhere. I tend to disagree with the statement that I have to assume these are Class 1 circuits, but I still am not certain what definately IS required to be marked as one.
A class one circuit uses chapter 3 wiring method, but the difference between it and power/lighting circuit is for the class 1 circuit no derating is required for conductor fill unless above 10% of the conductor ampacity.
But now that I think of it I have not see a PLC cabinet (UL508A) marked with the wiring type for field inputs and outputs. Inside the PLC cabinet 24 vdc is typically run with 120V...