There conditions where the boundary seal from a Class I, Division 2 location are not required to be standard explosionproof seals, but the code gives little guidance on what type of seal can be used, so many inspection authorities will require an explosionproof seal.
Seals at equipment that requires seals must always be explosionproof seals, even Division 2.
This is very interesting to me. What conduits/circuits would you be considering applying this to?I believe the area around a dispenser is considered class 1 div 2. Art 501.15 B 2 ..... such seals shall not be required to be explosion proof but shall be identified for the purpose of minimizing the passage of gas. Would this mean that it needs to be a seal off but doesnt need to be EP.
A far as I know there is only one product on the market that is actually so identified. That being Polywater's FST product.I believe the area around a dispenser is considered class 1 div 2. Art 501.15 B 2 ..... such seals shall not be required to be explosion proof but shall be identified for the purpose of minimizing the passage of gas. Would this mean that it needs to be a seal off but doesnt need to be EP.