Hi,
I'm new to this forum, but looking at some of the posts folks seem very knowledgeable here. I am overseeing the installation of a coating line into a class 1 div 1 location. The electrical cabinet is located outside of the hazardous area ~100ft from the machine, so all drive cables and IO need to be run into the classified area. We were thinking about running trough from the control cabinet to just outside the room, which is separated by a wall from the classified area, and then conduit from the trough, through the wall, into the classified room. I hit a snag in this plan when investigating multi-conductor cable and the seals.
The machine manufacturer has suggested several different Beldin Cable types ranging from VFD cable(29511) to multiconductor IO(27103A). I'm trying to figure out the different options from a cabling and sealing perspective to balance cost and complexity. These are the options as I see them.....
1. Use the suggested cable, breaking the multiconductor sheaths in the seals at the penetration into the classified area, and in non-intrinsically safe cases doing the same at the connection points with motors etc. Doing this I have questions around the 501.15.D.1 exception, as the VFD cable is shielded, I have encoder cables that are shielded twisted pair, and I have an ethernet cable. Can they each be sealed as a single conductor, or should they be broken apart? How do I interpret 'approved means to minimize the entrance of gasses....'?
2. Use a home run of MC-HL cable from my cabinet to the machine. This can eliminate any conduit runs, assuming I have cable tray or some way to support it. It also allows sealing as a single conductor at the area penetration point, and using the appropriate fittings to seal at the other end, it makes a clean installation. This stuff appears to be quite big and possibly cumbersome, as some of my cables are 25 conductor. Is it cost effective over conduit, seals, flex couplings, etc? I am interested in any experience you guys have with it.
3. Run the suggested cable in trough, hit a junction box outside the area, use MC-HL cable to penetrate the wall through conduit, which allows sealing as a single conductor. Once sealed, run the MC-HL in cable tray, and use appropriate MC-HL seals at the other end of the cables.
4. Just run single conductor wire from the cabinet to the machine. This gets messy fast, has potential noise issues with the VFD's (9 of them), but eliminates the multiconductor sealing issue.
Based on what I've read here, and what my electricians are telling me, sealing a multiconductor cable is difficult. Is it impossible? Also I am concerned with breaking the shield on the VFD and encoder cables, as the run is somewhat long and I don't want to introduce noise into the system.
I am looking for feedback on these options. Are they sound? Have I missed anything? Is there a better way? Any help would be greatly appreciated!
Thanks,
Jonathan
I'm new to this forum, but looking at some of the posts folks seem very knowledgeable here. I am overseeing the installation of a coating line into a class 1 div 1 location. The electrical cabinet is located outside of the hazardous area ~100ft from the machine, so all drive cables and IO need to be run into the classified area. We were thinking about running trough from the control cabinet to just outside the room, which is separated by a wall from the classified area, and then conduit from the trough, through the wall, into the classified room. I hit a snag in this plan when investigating multi-conductor cable and the seals.
The machine manufacturer has suggested several different Beldin Cable types ranging from VFD cable(29511) to multiconductor IO(27103A). I'm trying to figure out the different options from a cabling and sealing perspective to balance cost and complexity. These are the options as I see them.....
1. Use the suggested cable, breaking the multiconductor sheaths in the seals at the penetration into the classified area, and in non-intrinsically safe cases doing the same at the connection points with motors etc. Doing this I have questions around the 501.15.D.1 exception, as the VFD cable is shielded, I have encoder cables that are shielded twisted pair, and I have an ethernet cable. Can they each be sealed as a single conductor, or should they be broken apart? How do I interpret 'approved means to minimize the entrance of gasses....'?
2. Use a home run of MC-HL cable from my cabinet to the machine. This can eliminate any conduit runs, assuming I have cable tray or some way to support it. It also allows sealing as a single conductor at the area penetration point, and using the appropriate fittings to seal at the other end, it makes a clean installation. This stuff appears to be quite big and possibly cumbersome, as some of my cables are 25 conductor. Is it cost effective over conduit, seals, flex couplings, etc? I am interested in any experience you guys have with it.
3. Run the suggested cable in trough, hit a junction box outside the area, use MC-HL cable to penetrate the wall through conduit, which allows sealing as a single conductor. Once sealed, run the MC-HL in cable tray, and use appropriate MC-HL seals at the other end of the cables.
4. Just run single conductor wire from the cabinet to the machine. This gets messy fast, has potential noise issues with the VFD's (9 of them), but eliminates the multiconductor sealing issue.
Based on what I've read here, and what my electricians are telling me, sealing a multiconductor cable is difficult. Is it impossible? Also I am concerned with breaking the shield on the VFD and encoder cables, as the run is somewhat long and I don't want to introduce noise into the system.
I am looking for feedback on these options. Are they sound? Have I missed anything? Is there a better way? Any help would be greatly appreciated!
Thanks,
Jonathan