class 1 /div 1 junction box divider

Status
Not open for further replies.

mmccarter

Member
when placing a SSR in a class 1 div 1 jb is a divider required between the 24 vac control voltage and the 120/240 line voltage.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: class 1 /div 1 junction box divider

Originally posted by mmccarter:
when placing a SSR in a class 1 div 1 jb is a divider required between the 24 vac control voltage and the 120/240 line voltage.
Possibly - if the 24V side is a limited energy circuit.

You would also need to do if it was part of an IS circuit (not likely if it is 24VAC).
 

mmccarter

Member
Re: class 1 /div 1 junction box divider

Bob, Thanks for the responce, Have been away for a while. The situation is for a heater control relay for a class 1 div 1 area, where the relay would actuall be in a div 2 location.
Thanks Again
Marc
 