Is a splice, for termination of luminaire, made inside of a GUAT that is rated for the Class 1 / Division 1 area considered an arcing device?
My argument is that it is not an agnition source or arcing device and the contractor i am working for is requiring that i put a seal off on each and every luminaire inside of the C1 /D1 area.
I have sealed the area that enters the boundry.
I have sealed the toggle switches in listed C1 / D1 FS boxes.
I have used C1 / D1 listed GUAT fitting at each luminaire.
I have used C1 / D1 listed luminaires.
I have used rigid conduit, and have hard piped each luminaire.
I have used C1 / D1 unions for maintenence at each luminaire.
I have argued the article:501.15(A)(1)(1)(1)with an exception that states ?Seals shallnot be required for conduit entering an enclosure where such switches, circuitbreakers, fuses, relays, or resistors comply with one of the following: (1) Areenclosed within a chamber that is hermetically sealed against the entrance ofgasses or vapors.
What am I missing?
Any input on this matter will be greatly appreciated. About 30 - 3/4 EYS and the labor to install them worth.
Regards,
Bill
My argument is that it is not an agnition source or arcing device and the contractor i am working for is requiring that i put a seal off on each and every luminaire inside of the C1 /D1 area.
I have sealed the area that enters the boundry.
I have sealed the toggle switches in listed C1 / D1 FS boxes.
I have used C1 / D1 listed GUAT fitting at each luminaire.
I have used C1 / D1 listed luminaires.
I have used rigid conduit, and have hard piped each luminaire.
I have used C1 / D1 unions for maintenence at each luminaire.
I have argued the article:501.15(A)(1)(1)(1)with an exception that states ?Seals shallnot be required for conduit entering an enclosure where such switches, circuitbreakers, fuses, relays, or resistors comply with one of the following: (1) Areenclosed within a chamber that is hermetically sealed against the entrance ofgasses or vapors.
What am I missing?
Any input on this matter will be greatly appreciated. About 30 - 3/4 EYS and the labor to install them worth.