jfneidert

Member
Class 1 Division 1 Group C,D Environment:

Am terminating flexible cable into Explosionproof
motor peckerheads.

I know that seal connectors are not always required when using conduit, but what about flexible cord?

[ February 25, 2003, 11:38 AM: Message edited by: jfneidert ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Class 1, Div. 1 Motor Termination

Look at 501.5(D)(1) and 501.11(5). It appears that seals are required at the motor junction box.
Don
 

jfneidert

Member
Re: Class 1, Div. 1 Motor Termination

I came to the same conclusion, but am still puzzled why if I would have used a conduit smaller than 2", I wouldn't have been required to use a seal? (501.5 A 1)

Any ideas?

[ February 27, 2003, 02:30 PM: Message edited by: jfneidert ]
 