Electrical Systems Inspector
- Location
- Spotsylvania,Virginia
- Occupation
- Electrical Systems Inspector
I recently did some work at a autobody shop,they had a paint booth and paint mixing room installed. I had installed two XP receptacles and put a cord on the mixing rack motor. I was under the impression that this is a div 2 location because under normal operating conditions the containers are closed,therefore I used a non xp junction box at the motor, which by the way is XP. The inspector is calling it a div 1 location, on top of this he is requiring that the rack and table where the touch screen and scale are to be bonded to the screw I used to secure the XP receptacle box to the wall with #6 thhn to disapate static charge produced by the mixing of the paint. Is this a div 1 or 2 location, does nfpa 33 cover static issues?