G gfeuerborn New User Location Shawnee Occupation systems analyst Aug 24, 2020 #1 I have two meters to be wired together in a class 1 div 1 area. They are only about 3 feet apart. If I use seal offs at the meters, and flexible conduit do I meet requirements?
I have two meters to be wired together in a class 1 div 1 area. They are only about 3 feet apart. If I use seal offs at the meters, and flexible conduit do I meet requirements?
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Aug 24, 2020 #2 Flexible conduit is not suitable for Class I, Division 1. See Section 501.10(A).