I've done 2 of these in the last year, from what I remember, the hazardous area is only inside the tank. The way I did the installation was the most economical parts wise. For the intriscally safe wiring, use plastic j-box inside tank, and plastic cord connectors, then from there run PVC to control panel normal burial, use duct seal at the panel. For the pump feeds, run a 1" RMC about 12" long passing from the tank, to a seal-off fitting, after the fitting mount a plastic j-box, run the pump wires thru the seal-off and splice in j-box, then from there run PVC to control panel normal burial. And always use water proof wire nuts.