Hi trying to get some clarity on the requirements for alternators operating in Class 1 Div 2
For Zone 2 generators In Europe we use
Ex n Alternators
Built to comply with BS 5000 part 16. and EN50021: 1999 Certified Type EEx nA II T3 For use in Zone two Hazardous Areas
Automatic Voltage Regulator (AVR) is installed within an EEx d Zone 2 enclosure.
However keep coming up against IP56 TEFC alternators being used, however the manufacturers will not offer these as certificated for Haz Area use ?
My thoughts are that you should still use Ex product.
Rating range typically 10 - 150 kVA
Can anyone help clarify ??
Thanks
Jim