jcubedfire
New member
- Location
- Houston, TX
I have an explosion proof power panel located outdoors in a Class 1 Div 2 area, due to its location near a pump house. The conduits are sealed as they leave the box, then run outdoors ~ 150 feet into an MCC building. The Div 2 area extends about 20 feet past the box toward the MCC. Does Exception 4 to 501.15(B)(2) apply, such that a seal is not needed at the Div 2 boundary of the unclassified area? One of my associates felt that since the conduit eventually goes indoors at the MCC that item 2 of the exception would not apply. My opinion is that I can look at the segment of the conduit system as being entirely outdoors and the exception would apply.