What are the requirements for running conduit in the the slab of a class 1 division 2 location.
R ray_vega New member Location West Palm Beach, Fl, USA Aug 8, 2012 #1 What are the requirements for running conduit in the the slab of a class 1 division 2 location.
M mm11 Member Location Maryland Aug 8, 2012 #2 Grab your code book and read Article 501- it spells out what is acceptable for wiring methods and sealing.
Grab your code book and read Article 501- it spells out what is acceptable for wiring methods and sealing.
BPoindexter Inactive, Email Never Verified Location MT Vernon, WA Aug 8, 2012 #3 Specifically it is 501.10(B) for wiring methods and 501.15(C) for sealing. However you may need to also at other Articles/Sections depending on the type of installation i.e. dispensing station, bulk storage, etc. Last edited: Aug 8, 2012
Specifically it is 501.10(B) for wiring methods and 501.15(C) for sealing. However you may need to also at other Articles/Sections depending on the type of installation i.e. dispensing station, bulk storage, etc.