I saw dad pulling out the code book looking at the hazardous section and i started
asking questions. Now i am studying the hazardous code.
Dad showed me the ul rating certificate number for a design he is doing. i then went to the website and started reading.
My question is this, is a class 1 div 2 device such as a pushbutton ok to use in a class 2, div 1 area? i read in 500.7D that a purged/pressurized system would make
devices acceptable for the envorinment for devices that are not listed for the environment so i am going to say yes.
But would they be acceptable if you didn't have a purge/pressurized system?
Class 1 is a gas, but this is a class 2 dust. Doesn't the class 1 requirements make it satisfactory for class 2 since its more strict?
thanks in advance,
jimmy