steve holt
- Hawaii
Does the EYS used in a Class 1 Div 2 location need to be withing 18" of the floor where it enters, or above 18"
The condition is where the conduit enters the classified space through the floor and extends to devices above 18". Does the seal need to be within 18" vertically of where it enters or above 18"? One location is within an enclosed room and the other is at a storage tank located outdoors.If you are asking about a boundary seal, then any distance up to 10' is fine as long as there is no fitting between the boundary and the seal.
501.15(B)(2) Class I, Division 2 Boundary.
A conduit seal shall be required in each conduit run leaving a Class I, Division 2 location. The sealing fitting shall be permitted to be installed on either side of the boundary within 3.05 m (10 ft) of the boundary ... The conduit run between the conduit seal and the point at which the conduit leaves the Division 2 location shall contain no union, coupling, box, or other fitting except for a listed explosionproof reducer installed at the conduit seal. ...
thank youIt still appears to me that this is a boundary seal and that the floor is the boundary.