If you have a HPS light fixture in a class 1 div 2 group d location and the fixture is rated for a class 1 div 2 location but is not factory sealed does it need a seal at the fixture or just at the boundry limits?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Assuming the luminaire is otherwise properly installed in the Class I, Division 2 location, no additional enclosure seal is required. This would be analogous to any simple terminal box.

The identifying/marking requirements for luminaires can be confusing for Division 2 but, if the luminaire is already marked consistently with the location, the application is pretty straightforward.
 