Class 1 Div 2 Seal off requirements
Gategator37
Do T8 3 lamp fluorescent fixtures located in a Class 1 Div 2 area require seal offs? I know that 501.15(A)(1) states that a seal off is required for arcs, sparks, or high temperatures, would this be considered one? I would say know, but am unsure and would like to be better safe than sorry.
Thanks a lot.
seal offs are required when entering or existing the classified location. I don't believe you don't need a seal off for every fixture. The fixture has to rated
for classified location.
You were citing rules for Division 1. Make sure the luminaire is suitable for Division 2. See 501.130(B). If it isn't, seals won't make a difference. Don't confuse them with boundary seals.