Class 1 Div II Approved Motor Cabling Materials for 480V, 3 PH Motor Connections

Status
Not open for further replies.

Bob Lemke

Member
Location
Dayton, Ohio
Occupation
Controls Engineering
Getting some info on the possible use for a TC-ER rated cabling. This cable would exit through a perimeter barrier from a hazardous area to non-hazardous area through a conduit to be potted at final installation for a 10HP 480V, 3 PH motor connection. Looking for any other cable rated suggestions. Thank you.
 
Suitable alternate multiconductor cables are listed in Section 501.10(B)(1)(5).

BTW you have the Roman and Arabic numerals reversed; it's Class I, Division 2.
 