andy.sincali@nalasenginee
Member
- Location
- Norwich, CT
- Occupation
- Control System Engineer
I have been looking at some of the requirements for a class 1 Div 2 PLC Control Panel and based on some of the information that I have reviewed it appears that if all of the PLC equipment and associated terminal blocks are rated for the area (in my case Groups B,C,D that it does not matter what the actual enclosure is rated. My vendor/ contractor built a pump skid with a Nema4X Class 1 Div 2 SS Enclosure but ran wiring into the panel with no conduits or seals; basically just access holes through the bottom. Is this correct, (does it meet the NEC code)? and do you have any references regarding this issue.