I believe that is intended to say - if sliding contacts....switching mechanisms are employed, then it must be Div 1, as opposed to if Div 1 then it must have those components. Basically if there is anything that could arc/spark then it needs to be Div 1, otherwise it could be one of other constructions in (1) or (3) of that section.Ok, that makes sense.
I was looking at 501.125(B)(2), which seems to have an additional requirement that a motor have sliding contacts or some other type of switching ....
I'm not quite following why a Division 1 motor without any sliding or switching contacts couldn't be used in a Division 2 area. But the sump pump will have a float anyway, so I assume it does have sliding or switching contacts.
That would make a lot more sense.I believe that is intended to say - if sliding contacts....switching mechanisms are employed, then it must be Div 1, as opposed to if Div 1 then it must have those components. Basically if there is anything that could arc/spark then it needs to be Div 1, otherwise it could be one of other constructions in (1) or (3) of that section.
Not quite. Read the definition of identified; it does not necessarily mean listed or labeled. In fact, Section 501.125(A) lists several alternate constructions for motors in Division 1 that may or may not be listed. Really, really big motors are often one of the alternates and no NRTL has a standard other than NEMA MG-1 to certify it by. [NEMA MG-1 doesn’t require listing or labeling.]Any motor used in Class 1 Div 1 must be listed for the area of use. Any three phase motor can be used in Class 1 Div 2. A single phase 220 volt motor with a starting switch would require a motor rated Class 1 Div 1 and be suitable for the hazardous gas type. Any arcing device changes that area from Class 1 Div 2 to Div 1