Hi,
I have a project in a automotive shop and we are planning on installing our main electrical panels on the ground floor. (class 1 div 2).
I read sections 501 and 511.3(c).
If I mount the electrical panel at 18" AFF, do I have to worry about section 501 regarding conduits and fittings?
I have another situation. We have stub up coming from the concrete ground and the stub up is opening into a wireway. The wireway then leads to a electrical panel that is 18" AFF.
To make this situation work, can i put a flexible or rigid conduit with listed fittings per per NEC 501.10)B from the stub up to the electrical panel?
I have a project in a automotive shop and we are planning on installing our main electrical panels on the ground floor. (class 1 div 2).
I read sections 501 and 511.3(c).
If I mount the electrical panel at 18" AFF, do I have to worry about section 501 regarding conduits and fittings?
I have another situation. We have stub up coming from the concrete ground and the stub up is opening into a wireway. The wireway then leads to a electrical panel that is 18" AFF.
To make this situation work, can i put a flexible or rigid conduit with listed fittings per per NEC 501.10)B from the stub up to the electrical panel?