scottmarston
Member
- Location
- Meridian, ID
Hey all! I did a C1D2 project many years ago and have forgotten some of the painstaking fundamentals I figured out during that project. I've got a PanelView Plus HMI that indicates it is rated for a C1D2 environment. I'm mounting it on a NEMA 4X enclosure. Also mounted on the enclosure are two (2) hermetically sealed pushbuttons. The only thing I have on the backplane of the enclosure are terminal blocks.
My question is, can I just run 24VDC to it from a normal breaker? I know that they will have to seal the conduit when going from the safe area to the hazardous area. I shouldn't have to run the power for the HMI through an intrinsically safe barrier or some other galvanic isolator since all components are rated for C1D2, right?
Allen Bradley indicated that it was ok and they referenced a restricted breathing note:
Restricted Breathing: This is a form of sealing the enclosure with gaskets. The principle employed is that in Division 2 the enclosure is sufficiently tight that it is highly unlikely that a flammable cloud of gas would surround the enclosure for the length of time necessary for enough material to enter the enclosure to produce a flammable mixture.
My question is, can I just run 24VDC to it from a normal breaker? I know that they will have to seal the conduit when going from the safe area to the hazardous area. I shouldn't have to run the power for the HMI through an intrinsically safe barrier or some other galvanic isolator since all components are rated for C1D2, right?
Allen Bradley indicated that it was ok and they referenced a restricted breathing note:
Restricted Breathing: This is a form of sealing the enclosure with gaskets. The principle employed is that in Division 2 the enclosure is sufficiently tight that it is highly unlikely that a flammable cloud of gas would surround the enclosure for the length of time necessary for enough material to enter the enclosure to produce a flammable mixture.