Class 1 Division 2 Terminations

Status
Not open for further replies.

gryder

Member
Location
Indonesia
My company does engineering for a major oil company and the 'Company' representative has stated that a 'certified' increased safety terminal block is required in a NEMA 4 X enclosure for termination of lighting conductors. His reasoning is that the 'not certified' terminal block might vibrate loose and cause a spark. He can't seem to find the rule in the code and I can find nothing to contradict him. I've never known of this requirement or utilized such a device. However, I'm 67 years old (in my days we used wire nuts) I guess changes could have been made to the code. Any help appreciated
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Your client has probably been influenced by a European background.

There is no such rule in Article 501. There WOULD be such a rule in Article 505 if it were a true implementation of the IEC rules for Zones - which it isn't - which is why it isn't in Article 505 either.
 

jscottelwood

Member
Location
Oklahoma
terminations

terminations

I run into this a lot...the client is the one paying the bill so whatever they want, as long as it isn't a code violation, can be recommended. Remember, NFPA 70 (The NEC) is the minimum which is required. I have been given many fabrication and installation instructions which seem odd by our paying clients and as long as there is no code violation, I just tack in onto the bill (P, M and L) (sorry, Parts, Material and Labor).
 