Class 1 Division 2 TVSS unit.

Status
Not open for further replies.
Anybody know of a TVSS unit that can be used in a class 1 division 2 area? Either listed for that area, or carrying the nonincendive tag. Preferably DIN rail mount option, but at this point, I'll take what I can get.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Anybody know of a TVSS unit that can be used in a class 1 division 2 area? Either listed for that area, or carrying the nonincendive tag. Preferably DIN rail mount option, but at this point, I'll take what I can get.
See Section 501.35(B). Virtually nothing is listed for Division 2, but plenty of general purpose equipment is suitable for Division 2. [See 500.8(C)(6)(a)] BTW never look for nonincendive products for anything but instrumentation applications.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
It's the MOV that is "sealed." Ask your favorite, DIN mounted TVSS supplier for the MOV specs.
 