Class 1 Division II Air Craft Maintenance Hanger

Status
Not open for further replies.

KMeni

Member
Do Light Fixtures in Air Craft Maintenance Hanger need to be Explosion Proof?
Hanger Ceiling Height is at 90'
 
I say it depends on why type of aircraft and the size of the hanger, but, probably not.

NFPA 70

Article 513.3(C)

1 Aircraft Maintenance and Storage Hangars.
The area within 1.5 m (5 ft) horizontally from aircraft power plants or aircraft fuel tanks shall be classified as a Class I, Division 2 or Zone 2 location that shall extend upward from the floor to a level 1.5 m (5 ft) above the upper surface of wings and of engine enclosures.

2 Aircraft Painting Hangars.
The area within 3 m (10 ft) horizontally from aircraft surfaces from the floor to 3 m (10 ft) above the aircraft shall be classified as Class I, Division 1 or Class I, Zone 1. The area horizontally from aircraft surfaces between 3.0 m (10 ft) and 9.0 m (30 ft) from the floor to 9.0 m (30 ft) above the aircraft surface shall be classified as Class I, Division 2 or Class I, Zone 2.
 
Do Light Fixtures in Air Craft Maintenance Hanger need to be Explosion Proof?
Hanger Ceiling Height is at 90'
As a general rule, equipment outside a classified location does not need to be explosionproof. However, in Articles 511 to 516 there are rules, such as Section 513.7, for equipment outside the boundaries. A few of these rules apply to your installation but explosionproof fixtures are not required for the application you described.
 