MWh_Pro
Member
- Location
- Lakewood, CO
Hi All,
I am wondering whether I can just use Class 2 wiring methods (rather than Class 1) for a "rapid shutdown" feature for PV equipment. The behavior is described in NEC 2014, 690.12, where in the event of an emergency, there needs to be a button/switch that bring the voltage for PV output conductors down to 80V or less. I am now in the process of defining what wiring methods are best to use for the control circuits of such rapid shutdown appliances...
I like Class 2, because the wiring is affordable and can be run with communication circuits. But it seems that the functionality required of the circuit is very similar to that which is only reserved for Class 1 circuits:
Not quite sure if a PV rapid shutdown controller qualifies as "safety control equipment", but it feels like it.
Regardless of whether Class 1 or Class 2 is used, would it be a good idea to use CI (circuit-integrity) marked wires as well?
Thanks for the help!
Dave
I am wondering whether I can just use Class 2 wiring methods (rather than Class 1) for a "rapid shutdown" feature for PV equipment. The behavior is described in NEC 2014, 690.12, where in the event of an emergency, there needs to be a button/switch that bring the voltage for PV output conductors down to 80V or less. I am now in the process of defining what wiring methods are best to use for the control circuits of such rapid shutdown appliances...
I like Class 2, because the wiring is affordable and can be run with communication circuits. But it seems that the functionality required of the circuit is very similar to that which is only reserved for Class 1 circuits:
"725.31: Safety Control Equipment.
(A) Remote-Control Circuits. Remote-control circuits for safety control equipment shall be classified as Class 1 if the failure of the equipment to operate introduces fire or life hazard. ..."
(A) Remote-Control Circuits. Remote-control circuits for safety control equipment shall be classified as Class 1 if the failure of the equipment to operate introduces fire or life hazard. ..."
Not quite sure if a PV rapid shutdown controller qualifies as "safety control equipment", but it feels like it.
Regardless of whether Class 1 or Class 2 is used, would it be a good idea to use CI (circuit-integrity) marked wires as well?
Thanks for the help!
Dave