Hello!
I install a lot of Tesla wall connectors and Tesla recommends to use Neurio active energy monitor controller for applications like apartment building panels where it adjusts output based on usage.
I'm having a lot of issues with them passing inspections. As I expected just had another inspection for another installation and new set of issues arised. Inspector said that this device is "illegal". Even though he couldn't answer when I asked him how he passed these installations in the past.
Now got a "fail" for mixing class 1 and class 2 wiring. Inspector said that this device is illegal because :
A. CTs wiring (by Generac btw) are rated 300V and couldn't be in the same enclosure.
B. My com low voltage wire can't run in the same conduit as high voltage wire to the charger.
C. Tap conductor ground wire must be sized to the main wire ground size. 100A apartament breaker/feeder, my tap to the sub panel is #6 and #10 ground. He said that my tap ground to the sub panel has to be also #8?
He also didn’t like that Neurio energy monitor is located in the same enclosure of the panel.
I followed instructions from Tesla. Here is their installation/commissioning video:
I believe Neurio is made by Generac. Could anyone please help me to figure out the best way to approach this? Or this is actually illegal and all installations containing there for solar, powerwalls, generators are actualy illegal?
I install a lot of Tesla wall connectors and Tesla recommends to use Neurio active energy monitor controller for applications like apartment building panels where it adjusts output based on usage.
I'm having a lot of issues with them passing inspections. As I expected just had another inspection for another installation and new set of issues arised. Inspector said that this device is "illegal". Even though he couldn't answer when I asked him how he passed these installations in the past.
Now got a "fail" for mixing class 1 and class 2 wiring. Inspector said that this device is illegal because :
A. CTs wiring (by Generac btw) are rated 300V and couldn't be in the same enclosure.
B. My com low voltage wire can't run in the same conduit as high voltage wire to the charger.
C. Tap conductor ground wire must be sized to the main wire ground size. 100A apartament breaker/feeder, my tap to the sub panel is #6 and #10 ground. He said that my tap ground to the sub panel has to be also #8?
He also didn’t like that Neurio energy monitor is located in the same enclosure of the panel.
I followed instructions from Tesla. Here is their installation/commissioning video:
I believe Neurio is made by Generac. Could anyone please help me to figure out the best way to approach this? Or this is actually illegal and all installations containing there for solar, powerwalls, generators are actualy illegal?