hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have four fans 120V, 264VA single phase each and four heaters 24VAC, 40VA single phase each and 120VAC single phase for lights.
The panelboard is 120VAC so their is 3#10 from one 20A breaker to control panel then to fan, 3#10 from another 20A breaker to control panel to lights, 3#10 from one 20A breaker to control panel which has 120Vac to 24VAC transformer for heaters.
Now I have from control panel 3#10 for fans 120VAC, 3#10 for lights 120VAC and 2#12 from secondary if transformer 24VAC all in one conduit.
Questions:
1. Can you have 120VAC for light and power in same conduit as 24VAC?
2. 120VAC to 24VAC transformer require grounding?
3. Transformer 24VAC secondary has no EGC to heaters. Does it require EGC?
4. Would their be amapcity correction due to more than three current carrying conductor in the conduit all in one?