Class 2 circuit underground beneath parking lot

nhee2

Senior Member
Location
NH
Are there any exceptions/provisions that reduce the required cover on underground installation of a Class 2 or Class 3 circuit that is installed beneath a parking lot? I have looked through 725, and as best I can tell - the provisions of Table 300.5 still apply, and any Class 2 or 3, in conduit or direct-buried, needs to be 24" below grade.

Is there another section or exception that I am missing that would reduce this depth?
 

nhee2

Senior Member
Location
NH
See section 90.3
Do the rules in Article 725 reference burial depth?
As stated in the original post - i've looked through 725 and did not see anything. But was posting to see if there might be some provision that wasn't obvious to me.
 

nhee2

Senior Member
Location
NH
Ok. Thanks. That was my intent.

The wiring is ‘temporary’ meaning somewhere between 12 months and 12 years. There’s some pushback on applicability of table 300.5, which was the reason for the question.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
725.3 says only the requirements of Article 300 that are specifically referenced in Article 725 apply to those installations. 300.5 is not found in Article 725.
 

nhee2

Senior Member
Location
NH
725.3 says only the requirements of Article 300 that are specifically referenced in Article 725 apply to those installations. 300.5 is not found in Article 725.
Note it is referenced for Class 1 circuits (725.46 says to install in accordace with Part I of Chapter 300). But not for the Class 2 and 3 circuits I was asking about.
 