Are there any exceptions/provisions that reduce the required cover on underground installation of a Class 2 or Class 3 circuit that is installed beneath a parking lot? I have looked through 725, and as best I can tell - the provisions of Table 300.5 still apply, and any Class 2 or 3, in conduit or direct-buried, needs to be 24" below grade.
Is there another section or exception that I am missing that would reduce this depth?