Hello everyone,
I have a quick question on class 2 circuits. I have seen a new product that has come out that has a single 120VAC/24VAC 500VA transformer with (5) 4Amp circuit breakers on the secondary side. Since the secondary side has 4Amp circuit breakers (essentially cutting the load side into (5) 100VA sections) the supplier is suggesting that this product can supply power for class 2 circuits. I have looked at Table 11(A) in Chapter 9 of the 2014 NEC and it states that a class 2 power source for 21VAC through 30VAC can only have a maximum nameplate rating of 100VA. I am thinking that this new product would not retain a class 2 circuit rating since the transformer is 500VA. Is my logic correct or am I missing something else in the code that allows a circuit breaker to trump the nameplate rating of the power source.
Thanks for any help,
Brian Z.
I have a quick question on class 2 circuits. I have seen a new product that has come out that has a single 120VAC/24VAC 500VA transformer with (5) 4Amp circuit breakers on the secondary side. Since the secondary side has 4Amp circuit breakers (essentially cutting the load side into (5) 100VA sections) the supplier is suggesting that this product can supply power for class 2 circuits. I have looked at Table 11(A) in Chapter 9 of the 2014 NEC and it states that a class 2 power source for 21VAC through 30VAC can only have a maximum nameplate rating of 100VA. I am thinking that this new product would not retain a class 2 circuit rating since the transformer is 500VA. Is my logic correct or am I missing something else in the code that allows a circuit breaker to trump the nameplate rating of the power source.