I have been given the task of quoting a controls system for Class 2, Div. 1, Group G.
502.1 states exp. proof equip. and wiring shall not be required and shall not be acceptable in Class2 locations unless it is identified for those locations.
The control panel will be outside on the top of a grain elevator. NEMA 4 in addition to 7 and/or 9 (not sure which). Do the components INSIDE the box have to be rated for the environment or just the conduit and box.
The components inside the box will be wired to field devices inside the grain bin where the dust is present (div.1 location). The enclosure itself is mounted in a non hazardous location.
I am confused~if it is not required does that mean I don't have use it or what.
502.1 states exp. proof equip. and wiring shall not be required and shall not be acceptable in Class2 locations unless it is identified for those locations.
The control panel will be outside on the top of a grain elevator. NEMA 4 in addition to 7 and/or 9 (not sure which). Do the components INSIDE the box have to be rated for the environment or just the conduit and box.
The components inside the box will be wired to field devices inside the grain bin where the dust is present (div.1 location). The enclosure itself is mounted in a non hazardous location.
I am confused~if it is not required does that mean I don't have use it or what.