Is a class 2 power limited circuit required to be in conduit?
dnem said:How about Honeywell CL-2 wiring ran in the wall for LV cabinet lights ?
David
CL2 ran inside the wall cavity to supply LV lighting [411.4(A)] can be run in a conduit raceway [411.4(A)(1)] or follow the requirements of 725.52 [411.4(A)(2)]
The "listed Class 2 power source" of 411.4(A)(2) must comply with Table11(A) & (B) of chapter 9 on page 638. Note the amperage limitation of the power supply. Power supply will be inspected on final.
hbiss said:The "listed Class 2 power source" of 411.4(A)(2) must comply with Table11(A) & (B) of chapter 9 on page 638. Note the amperage limitation of the power supply. Power supply will be inspected on final.
First, I assume you have adopted the 2005 NEC. Second I assume you have the test equipment to perform the required testing to see that the power supply conforms to Table 11.
Better idea: Just look to see that the power supply label says "CL2 wiring may be used" or just CL2. If it does not the wiring must be a class 1 method.
-Hal